2-wire systems can be 120 volts (Hot to Neutral), or rarely in the USA they can be 240 volts (Hot to Hot), or commonly in foreign countries they can be 230 volts (Hot to Neutral). Metering of these systems can be done with any of our Omnimeter models. Metering 120 volt 2-wire systems can also be accomplished using our EKM-15IDS or EKM-15E, but the instructions below will focus on the EKM Omnimeters.
- Do I want to read the meter(s) locally with computer or do I want a cloud based solution (EKM Push).
- What diameter and amperage rating will I need for the Current Transformers? You will need one CT for your 2-wire single phase electrical system.
- Do I need to go wireless?
- Do I have a need to daisy chain multiple Omnimeters together? This allows you to connect multiple Omnimeters in series, which can then be connected to a single communication device.
Connection Instructions:
For a 120 volt 2-wire system or a 230 volt 2-wire system (1 hot, 1 neutral) you will only need to use 1 CT. You will have 1 hot wire (commonly black or red) and a neutral wire (usually white). When you measure the voltage between these 2 wires you will get 120 volts, or 230 volts for those systems not in the U.S.
- Turn off power to the sub-panel.
- Connect the hot line voltage reference wire to port 7 on the Omnimeter and the Neutral line voltage reference wire to port 10 on the Omnimeter.
- Connect the CT so that the hot wire passes through it and the arrow on the CT points towards the load.
- Connect the CT black wire to port 1 on the Omnimeter and the CT white wire to port 2 on the Omnimeter.
For a 240 volt 2-wire system (2 Hots, no neutral) you will only need to use 1 CT. When you measure the voltage between these 2 wires you will get 240 volts.
- Connect the L1 line voltage reference wire to port 7 on the Omnimeter
- Connect the L2 line voltage reference wire to port 10 on the Omnimeter.
- Connect the CT so that L1 passes through it and the arrow on the CT points towards the load.
This video tutorial provides an example of how to install an Omnimeter Pulse v.4 on a 120/240v electrical system. You can use this video to infer how a single phase, two wire installation might go. The only absolute difference is that there will only be one CT and one voltage reference wire:
See this model for reference of how to properly connect an Omnimeter to a 2-wire system:
Here is a link to a movable 3D model of the above diagram that you can use to see details of any side: 2-wire Single Phase EKM Omnimeter 3D Model