TABLE OF CONTENTS
- Connection Instructions
- Omnimeter I v.3 Diagram
- Omnimeter II UL v.3 Diagram
- Omnimeter Pulse v.4 Diagram
- Omnimeter Pulse UL v.4 Diagram
3-phase 3-wire systems have 3 hot wires and NO neutral wire. These are generally older 3-phase circuits. You will need 1 Omnimeter and only 2 CTs for this kind of a system. Metering of these systems can be done with any of our EKM Omnimeter models up to 415VAC. For metering 3-phase 3-wire systems above 415VAC you would need to use our Omnimeter HV v.4, which is capable of metering up to 600VAC.
The loads must be balanced on all three phases in order to meter a 3-phase 3-wire circuit accurately.
If you are wondering why you only need 2 CTs for a 3-phase system you can consult Blondel's Theorem
- Do I want to read the meter(s) locally with computer or do I want a cloud based solution (EKM Push3).
- What diameter and amperage rating will I need for the Current Transformers? You will need two CTs for your 3-phase 3-wire electrical system.
- Do I need to go wireless?
- Do I have a need to daisy chain multiple Omnimeters together? This allows you to connect multiple Omnimeters in series, which can then be connected to a single communication device.
Connection Instructions:
For a 3-phase 3-wire system you will need to use 2 CTs. You will have 3 hot wires and NO neutral wire.
- Turn off power to the sub panel.
- Mark one of the hot wires as L1, mark the second wire as L2, and mark the last hot line as L3. You can pick these randomly.
- First, install a jumper wire from port 8 on the Omnimeter to port 10 on the Omnimeter. Connect the L1 hot line voltage reference wire to port 7 on the Omnimeter, connect the L2 hot line voltage reference wire to port 8 on the Omnimeter and connect the L3 hot line voltage reference wire to port 9 on the Omnimeter.
- Connect the CT1 so that the L1 hot wire passes though it and the arrow on the CT points towards the load. Connect the CT3 so that the L3 hot wire passes though it and the arrow on the CT points towards the load.
- Connect the CT1 black wire will go to port 1 on the Omnimeter and the CT1 white wire will go to port 2 on the Omnimeter. Connect the CT3 black wire will go to port 5 on the Omnimeter and the CT2 white wire will go to port 6 on the Omnimeter.
When this meter is properly connected it will read volts and current on L1 and L3, but will read 0 volts and current on L2.
This video tutorial provides an example of how to install an Omnimeter Pulse v.4 on a 120/240v electrical system. You can use this video to infer how a three phase, three wire installation might go. For this type of electrical system the CT and voltage reference wiring will be different so refer to the diagram above for that information:
Below are diagrams showing each Omnimeter model wired to a 3-phase 3-wire (no neutral) electrical system, while also being RS-485 hardwired to a Push3 gateway (A to A, B to B).
Omnimeter I v.3:
Omnimeter II UL v.3:
Omnimeter Pulse v.4:
Omnimeter Pulse UL v.4:
See this model for reference of how to properly connect an Omnimeter to a 3-phase 3-wire system: